5kW Off-Grid Solar System + Diagrams, Consumption
🎁 Free Diagrams: cleversolarpower.com/free-diagrams/
📖 My Best-Selling book on Amazon: cleversolarpower.com/off-grid-solar-power-simplified
Work with me: cleversolarpower.com/product/solar-system-review-service
Parts:
Solar Panels (12x): cleversolarpower.com/go/CS400W
Battery: cleversolarpower.com/go/EG448V (cheaper version)
Charge Controller: cleversolarpower.com/go/450/100
Inverter/Charger: cleversolarpower.com/go/5000VA
Alternative with UL listing: cleversolarpower.com/go/3000VAUL
Generator: amzn.to/3W4zjxr
Solar PV cable: amzn.to/4eQcYv1
4AWG welding cable: amzn.to/4buslX9
DC Breaker (2x): amzn.to/3L9Ql74
125A Class-T fuse: amzn.to/3XJPUaX
Class-T fuse holder: amzn.to/4cgihlD
In this video, I'm going to walk you through a complete 5kW off-grid solar system, covering everything from selecting the right components to understanding the overall costs. We'll break it down into three simple steps and give you all the details you need, including a 5kW solar diagram.
We'll start by choosing the solar panels and charge controller, then move on to sizing the battery, and finally, we'll choose the inverter and generator. I'll also provide a detailed wiring diagram with wire sizes and fuses, explain what this system can run, and break down the total cost.
Topics Covered:
1. Choosing Solar Panels and Charge Controller: Learn how to select the right solar panels and a 100A charge controller for a 5kW off-grid solar system.
2. Sizing the Battery: Find out how to size your battery to store enough energy for your needs. We’ll use three 48V 100Ah server rack batteries.
3. Choosing an Inverter and Generator: Discover why the Victron Multiplus 48V 5000VA inverter and Honda 3000W generator are great choices for this setup.
4. Wiring Diagram with Wire Sizes and Fuses: Get a detailed 5kW solar diagram showing the wiring and fuses needed for safe and efficient operation.
5. What Can It Run?: See a practical example of the daily energy consumption this system can handle, perfect for tiny houses or cabins.
6. Cost of the System: Understand the total cost of a 5kW solar system with battery, including all components and installation materials.
The total cost for this 5kW solar system with battery is approximately $12,000.
Переглядів: 19 948

Відео

How Many Solar Panels to Charge a Battery?
Переглядів 23 тис.День тому
🎁 Free Diagrams: cleversolarpower.com/free-diagrams/ My Best-Selling book on Amazon: cleversolarpower.com/off-grid-solar-power-simplified In this video, I'm going to show you how to determine how many solar panels you need to charge a 12V 100Ah lithium battery. To recharge this battery, you'll need 400W of solar panels. I’ll break it down into three simple steps: 1. Finding out battery capacit...
7 Mistakes For Off-Grid Solar Power Systems - Avoid These!
Переглядів 37 тис.День тому
🎁 Free Diagrams: cleversolarpower.com/free-diagrams/ My Best-Selling book on Amazon: cleversolarpower.com/off-grid-solar-power-simplified Work with me: cleversolarpower.com/product/solar-system-review-service/ In this video, I'm going to show you the 7 common mistakes beginners make when building their own off-grid solar systems. Avoid these pitfalls to ensure your DIY solar project is efficie...
Best Budget Off-Grid Inverter - Giandel 600W Inverter Review
Переглядів 4 тис.Місяць тому
Giandel 600W Inverter: amzn.to/3VdS4Nl 6AWG welding cable: amzn.to/4aRyR9X 70A MIDI fuse: amzn.to/4aOdEh1 🎁 Free Diagrams: cleversolarpower.com/free-diagrams/ My Best-Selling book on Amazon: cleversolarpower.com/off-grid-solar-power-simplified In this video, I'm going to review the Giandel 600W off-grid inverter. This is not a sponsored video; I bought this inverter with my own money to provid...
Prevent Galvanic Corrosion on Your Boat: Galvanic Isolators Vs. Isolation Transformers
Переглядів 1,4 тис.Місяць тому
🎁 Free Diagrams: cleversolarpower.com/free-diagrams/ My Best-Selling book on Amazon: cleversolarpower.com/off-grid-solar-power-simplified 30A galvanic isolator: amzn.to/3wUESEO Isolation transformer: amzn.to/3wW7duE Work with me: cleversolarpower.com/product/solar-system-review-service/ In this video, I'm going to show you everything you need to know about galvanic corrosion protection for you...
Off Grid Solar System Design: 4 Easy Steps + Diagram
Переглядів 28 тис.Місяць тому
🎁 Free Diagrams: cleversolarpower.com/free-diagrams/ My Best-Selling book on Amazon: cleversolarpower.com/off-grid-solar-power-simplified My done for you service: cleversolarpower.com/product/solar-system-review-service/ Parts: 10x 250W solar panels: cleversolarpower.com/go/san10x250w 12V 200Ah battery from Redodo. cleversolarpower.com/go/red12v200ah use code 'clever' for a 5% discount 150V/60...
Low Frequency Vs. High Frequency Inverters
Переглядів 20 тис.Місяць тому
🎁 Free Diagrams: cleversolarpower.com/free-diagrams/ My Best-Selling book on Amazon: cleversolarpower.com/off-grid-solar-power-simplified In this video, I'm going to show you the difference between low vs high frequency inverters, focusing on their efficiency and advantages. We'll dive into various criteria such as weight, applications, lifespan, and price to help you determine which type is b...
Inverter Standby Power Consumption
Переглядів 13 тис.Місяць тому
🎁 Free Diagrams: cleversolarpower.com/free-diagrams/ My Best-Selling book on Amazon: cleversolarpower.com/off-grid-solar-power-simplified In this short video, I'm going to show you the silent energy consumer of your off-grid solar system: the inverter standby power consumption. We'll dive into the details of low power consumption inverters and how to manage inverter idle consumption effectivel...
Van Electrical System Diagrams - Campervan Electric 12V/24V
Переглядів 9 тис.Місяць тому
🎁 Free Diagrams: cleversolarpower.com/free-diagrams/ My Best-Selling book on Amazon: cleversolarpower.com/off-grid-solar-power-simplified 105°C welding cable: amzn.to/3OCo4s0 MRBF Fuse Terminal: amzn.to/3NWGcfZ Litime 12V 230Ah Battery: amzn.to/4dDsMkd DC to DC Charger: amzn.to/4bm3h59 or amzn.to/3wt1Q60 In this video, I'm going to simplify van electrical systems for you, breaking down everyth...
How Many Batteries for 5kW Solar System
Переглядів 46 тис.Місяць тому
🎁 Free Diagrams: cleversolarpower.com/free-diagrams/ My Best-Selling book on Amazon: cleversolarpower.com/off-grid-solar-power-simplified In this video, I'm going to show you how many batteries you need for a 5kW solar system. If you have an off-grid cabin with a 5kW solar panel system. You need to use this website: pvwatts.nrel.gov/ to find out the minimum amount of sunhours you have at your ...
What Size Inverter for 100Ah Battery - Sizing Battery for Inverter
Переглядів 15 тис.2 місяці тому
🎁 Free Diagrams: cleversolarpower.com/free-diagrams/ My Best-Selling book on Amazon: cleversolarpower.com/off-grid-solar-power-simplified Victron Phoenix 12V 1200VA Inverter: cleversolarpower.com/go/CC12V1200VA In this video, I talk about what size inverter for 100Ah battery. Join me as I break down the complexities and provide straightforward answers to crucial questions like what size invert...
Complete Off-Grid Solar System With Batteries for Homes - EG4 6000XP for $12,340
Переглядів 16 тис.2 місяці тому
🎁 Free Diagrams: cleversolarpower.com/free-diagrams/ My Best-Selling book on Amazon: cleversolarpower.com/off-grid-solar-power-simplified - 540W Solar panels: cleversolarpower.com/540W - EG4 Batteries: cleversolarpower.com/EG4-30kW - EG4 Inverter: cleversolarpower.com/EG4-6000XP - 7600W Inverter/generator: amzn.to/4b2VbOr - 105°C Welding cable: amzn.to/3OCo4s0 In this video, I'm diving deep in...
How Does Off Grid Solar Work - Explained with Diagrams
Переглядів 41 тис.2 місяці тому
🎁 Free Diagrams: cleversolarpower.com/free-diagrams/ My Best-Selling book on Amazon: cleversolarpower.com/off-grid-solar-power-simplified This video is your guide to understanding how off-grid solar works. From the simplicity of a single solar panel system to the robustness of a hybrid inverter setup, I cover it all: - Discover the basics with an off-grid solar diagram that starts with just on...
How Much Power Does A 100W Solar Panel Produce?
Переглядів 92 тис.2 місяці тому
🎁 Free Diagrams: cleversolarpower.com/free-diagrams/ My Best-Selling book on Amazon: cleversolarpower.com/off-grid-solar-power-simplified 100W solar panel: amzn.to/3WeBIpZ 12V 50Ah battery: amzn.to/3Uf3D7H 10A charge controller: amzn.to/3VYJIem DC fusebox: amzn.to/3VV0bAa 6ft Solar cables: amzn.to/3PZvfeC Wiring: amzn.to/44cRuDL Fuses: amzn.to/49xLhDd Inverter: amzn.to/4av9RFX More recommended...
How Many Solar Panels to Run a House Off Grid?
Переглядів 110 тис.2 місяці тому
How Many Solar Panels to Run a House Off Grid?
Why An Electric Car With Solar Panels is A Bad Idea
Переглядів 16 тис.3 місяці тому
Why An Electric Car With Solar Panels is A Bad Idea
How To Use Solar Panels Directly Without Battery - Off-Grid
Переглядів 354 тис.3 місяці тому
How To Use Solar Panels Directly Without Battery - Off-Grid
How Long Can a 12V Battery Run a TV? - 12V 100Ah Lithium
Переглядів 103 тис.3 місяці тому
How Long Can a 12V Battery Run a TV? - 12V 100Ah Lithium
How Many Solar Panels To Run a Fridge/Freezer?
Переглядів 608 тис.3 місяці тому
How Many Solar Panels To Run a Fridge/Freezer?
Connecting Batteries in Series - Charging 12V Lithium Batteries
Переглядів 39 тис.3 місяці тому
Connecting Batteries in Series - Charging 12V Lithium Batteries
Load Shedding Solution for South-Africa - Eskom DIY UPS
Переглядів 4,9 тис.3 місяці тому
Load Shedding Solution for South-Africa - Eskom DIY UPS
Replace Lead Acid Battery With Lithium (LiFePO4)
Переглядів 16 тис.4 місяці тому
Replace Lead Acid Battery With Lithium (LiFePO4)
Charging Lithium Batteries With Alternator - Howto Guide
Переглядів 48 тис.4 місяці тому
Charging Lithium Batteries With Alternator - Howto Guide
How to Charge Batteries in Parallel With Different Capacity
Переглядів 75 тис.4 місяці тому
How to Charge Batteries in Parallel With Different Capacity
Different Types of Inverters for Solar Power Systems
Переглядів 18 тис.4 місяці тому
Different Types of Inverters for Solar Power Systems
Difference Between Grid-Tied, Off-Grid, and Hybrid AC and DC Coupled Solar Systems
Переглядів 14 тис.4 місяці тому
Difference Between Grid-Tied, Off-Grid, and Hybrid AC and DC Coupled Solar Systems
How To Size a Wire For Off-Grid Solar Power - Calculation Examples
Переглядів 16 тис.4 місяці тому
How To Size a Wire For Off-Grid Solar Power - Calculation Examples
How to Size Fuses For Off Grid Solar System
Переглядів 8 тис.4 місяці тому
How to Size Fuses For Off Grid Solar System
Fridge Power Consumption - How Much Power Does my Fridge Consume
Переглядів 10 тис.4 місяці тому
Fridge Power Consumption - How Much Power Does my Fridge Consume
Adding a Backup Generator to Off-Grid Solar System
Переглядів 8 тис.4 місяці тому
Adding a Backup Generator to Off-Grid Solar System

КОМЕНТАРІ

  • @yevgenygritsayenko1311
    @yevgenygritsayenko1311 5 годин тому

    I use on-grid invertor in combination with of-grid invertor (pure sine) when the main grid is off. Just need to use sensor on the wire from of-grid invertor, which controls used power, so limiter in on-grid invertor controls generated power to compensate load for of-grid inverter

  • @thelonewolf666
    @thelonewolf666 6 годин тому

    garbage--- a solar panel needs a battery to turn on regulator or they will not work

  • @RossWood-sl5oj
    @RossWood-sl5oj 9 годин тому

    When you refer to Lead Acid batteries are you also referring to AGM Absorbed glass matt or Gel batteries also, as I understand they have quite differing characteristics to conventional 'wet cell' Lead acid batteries, ie less resistance, larger charge rates and deeper cycling 50%

    • @RossWood-sl5oj
      @RossWood-sl5oj 9 годин тому

      sorry continuing :deeper cycling 50% than a conventional wet cell battery at 20% discharge safely for maximum lifespan. AGM or Gel batteries obviously have more capacity than conventional wet cell L/A's.

  • @yuriy5514
    @yuriy5514 11 годин тому

    Thank you

  • @karinabourne3465
    @karinabourne3465 20 годин тому

    I have a question about inverters and batteries. I’m renovating my caravan with 240v wires throughout. I only plan to run a fridge, convection oven, lights and a tv and dvd player. The fridge will be the only one running non stop (while travelling around). The fridge is 240v 50Hz 0.73A 106W. How do I work out what size inverter and battery do I need?

    • @cleversolarpower
      @cleversolarpower 19 годин тому

      I advice against a convection over. It draws a lot of power. For the fridge, multiply the power consumption by 8 hours, which is a 30% duty cycle. 106W*8h=850Wh I made a video about system design, look it up on my channel page.

  • @wagohowardmusic
    @wagohowardmusic 23 години тому

    Thoughts on pwrinv250024w aims inverter?… mine just started high pitch noise solid why?

    • @cleversolarpower
      @cleversolarpower 19 годин тому

      It possible that low frequency inverters make this sound. If it did not do this before with a load attached, you might want to check for loose components or mounting it differently to minimize vibrations.

    • @wagohowardmusic
      @wagohowardmusic 14 годин тому

      @@cleversolarpower excellent advice. I’ll make sure all connections are tight. I can upload a video… to my channel and leave it up for a day or so and then remove.. if you have time to take a peek- Used hardy board backer. Attached Mr. power solar inverter middle of the road inverter not too cheap not too expensive to a battery using recommended gauge 14 , then connected battery to inverter using larger wire 8aug, two deep cycle, 12 V batteries, wired and series and then ran one solar pan… Left refrigerator on to see if it would work overnight and woke up to allow whining, caution, warning tone my best estimate is it depleted the battery however, the meter read 20 V still… I was under the impression you could drain a cycle battery down to 70%.. Thank you very much for taking the time. I enjoy your channel.

  • @kamilzarzycki7163
    @kamilzarzycki7163 23 години тому

    I just bought a 60A MPPT controller for a campervan, and in the instruction it says that I need 6 mm diameter wire for a controller, but my solar panels (450W and 120W) have 4 mm diameter wire:/

    • @cleversolarpower
      @cleversolarpower 22 години тому

      The wire size in and out of the charge controller is different. The wire going in the battery will have to be thicker because there is more current. Power= voltage*current

  • @pissedoffpuppy
    @pissedoffpuppy День тому

    Finally ordered your book😁🤙🏽

  • @Fatpumpumlovah2
    @Fatpumpumlovah2 День тому

    who the fuq has only 3 hours of sun per day?!

    • @cleversolarpower
      @cleversolarpower День тому

      Sunhours, not hours of sun. Watch the whole video on my channel page.

  • @davet9633
    @davet9633 День тому

    Victron 5000 is not UL listed; thus, not a good choice in CO (if you want insurance to cover any issues).

    • @cleversolarpower
      @cleversolarpower 19 годин тому

      Victron 48V MultiPlus-II UL1741 3kVA 120V is UL listed. You can place two in parallel to get 6kW of output. I linked it in the description.

  • @konkaragounakis5924
    @konkaragounakis5924 День тому

    Excellent thankyou simple easy to understand 👍

  • @zzz5824
    @zzz5824 День тому

    The battery shuts down at 10volts.. It doesn’t run the whole way down, scam

  • @grahamjohnbarr
    @grahamjohnbarr День тому

    You must explain that a 3000W Inverter is Peak. The Inverter is only safe to 1500W.

    • @cleversolarpower
      @cleversolarpower 19 годин тому

      Define 'safe'

    • @grahamjohnbarr
      @grahamjohnbarr 9 годин тому

      @@cleversolarpower Wrong word. Would continuous operation up to 1500W be better. The 3000W is only for a short period of time. I do believe the advertising should state the Inverter is a 1500W with a Peak of 3000W. I have an 8000W Modified Sine Wave Inverter, it is designed to run, according to my manual, at a maximum of 4000W with a Peak of 8000W for <30 seconds. This would be correct as I found this out the hard way & had to replace a 10k ohm, 10W resistor that had blown. Any reply to my inquiry on the best place to put the input Voltage to the Batteries from the Controller as regards the output Voltage going to the Inverter. Can I attach the Leads to the same place? I do like your presentations, Thank you.

  • @chaklungmailcom
    @chaklungmailcom День тому

    36.8Voc x 1.25 = nonsence, indeed, why use temp coefficients for panels that manufacturers measure and publish? Why take into account the installation method? OMG

  • @ihabahmed1132
    @ihabahmed1132 День тому

    Very good analysis and guidelines, i will be happy i you do a video to How Many Solar Panels To Run a 1.0/1.5 ton Air conditioner.

    • @cleversolarpower
      @cleversolarpower 19 годин тому

      This one is in the making ✌Appreciate your sub!

  • @ludvigj6130
    @ludvigj6130 2 дні тому

    Amazing video! I am trying to make a simple solar heating system for my spa (just 700litres) with a 12v 18w pump powered by a 25w solar panel. When i connect the panel directly to the pump it works great when the sun is shinging but when it isnt it just makes a whining noise. Which i guess might damage the motor. Do you have any advice? Do you think a buck co verter would solve this problem? I would really really appreciate some help!

    • @cleversolarpower
      @cleversolarpower 19 годин тому

      18W is very low for a pump, so i guess it's just for circulation. I recommend getting another 25W panel or one 50W panel. Then use a buck or PWM converter directly with the panels.

  • @shermanramsingh7898
    @shermanramsingh7898 2 дні тому

    how do you connect enough EP3 Cube to give you a battery bank of 350kw

    • @cleversolarpower
      @cleversolarpower 19 годин тому

      Easy, just divide by the power capacity of one battery which is 3.3kWh

  • @travisd7888
    @travisd7888 2 дні тому

    I recently got a Jupiter 3000w power inverter, Super Start Marine Deep Cycle battery, Viking 4amp battery charger/maintainer; all recommended to compliment each other. Is this a good setup?

    • @cleversolarpower
      @cleversolarpower 2 дні тому

      Compliment? That's a bit of an overstatement. I would say compatible 😬

  • @NerdThingsAndMore
    @NerdThingsAndMore 2 дні тому

    Thanks for the info and video

  • @gd2329j
    @gd2329j 2 дні тому

    Just a heads up for the new guys . ** NEVER PARALLEL THE INVERTER OUTPUTS **

    • @cleversolarpower
      @cleversolarpower 2 дні тому

      * if it's a off grid inverter. Sounds like you have experience with it 😉

  • @1GREATDANE
    @1GREATDANE 2 дні тому

    24 Volt 3.8K Lithium Iron Phosphate Big Battery with 100amp BMS Handle a Victron Phoenix 24/1200 Inverter or a WZRELB 24 Volt 2500 Watt Inverter ??

    • @cleversolarpower
      @cleversolarpower 19 годин тому

      1200VA/24V=50A -> yes, 2500W/24V=104A -> no (if you draw the full 2500W)

  • @KGopidas
    @KGopidas 2 дні тому

    Informstive, buht the point rem a ins rhat if attempting an implementation why not realise entire potential?. If we install A battery snd connect yhe fridge yhrough ig, ee improve power factor snd therefore consume less?

  • @mopikozz
    @mopikozz 2 дні тому

    Why do i use some people using DC circuit breaker instead of fuse? Isnt DC breaker better in the sense its not single use?

    • @cleversolarpower
      @cleversolarpower День тому

      Normally we use fuses with DC because it's cheaper. And they are not blowing. AC breakers can blow more often so we use breakers.

  • @ihabahmed1132
    @ihabahmed1132 2 дні тому

    Very Nice Explanation Thank You for sending The Free Diagrams 💐🎁

  • @graphguy
    @graphguy 2 дні тому

    Yesterday I saw a video that shocked me. on traditional panels --- ANY shade shatters the pv output. The video demonstrated that even a 5% coverage of shade dropped the output from 93w down to 17w. What do you say?

    • @cleversolarpower
      @cleversolarpower 2 дні тому

      It's true. If you look closely at a solar panel there are cells in series. If one cell receives less irradiance, the current will drop. And the panel will take on the cell with the lowest current.

  • @Supanova70
    @Supanova70 2 дні тому

    Questtion on this MPPT controller. I hae 2 house to start batteries on my boat. Got to the boat and app said they were floating. Showed 20v from 2 100 watt panels 0 amps. When my boat is running my battery monitor shows -1.59 amp draw? Why? The voltage is 14.8 from motors. Shunt is installed correct to a neg bus bar. All house loads are off during readings. This also has a ACR

    • @cleversolarpower
      @cleversolarpower 19 годин тому

      It's the idle consumption of your inverter. If you turn off the inverter, the reading will drop.

  • @IMMUSLIM1000
    @IMMUSLIM1000 3 дні тому

    4288 kwh or wh???

    • @cleversolarpower
      @cleversolarpower 2 дні тому

      It's European notation of the decimal which is a comma (,). That's why there is so many confusion.

  • @user-uj8qu1gz1y
    @user-uj8qu1gz1y 3 дні тому

    Wow! Interesting . I want . Because my bill is 6,500 pesos around 450 watts used

    • @cleversolarpower
      @cleversolarpower 3 дні тому

      If you are grid-tied i recommend using a string inverter to offset you energy consumption. Especially if you have a feed in tariff.

    • @user-uj8qu1gz1y
      @user-uj8qu1gz1y 2 дні тому

      @@cleversolarpower hi. What’s string inverter ? Thank you

  • @linossinkala7840
    @linossinkala7840 3 дні тому

    Thankyou sir

  • @GlobalSolarEnergyPakistan
    @GlobalSolarEnergyPakistan 3 дні тому

    Good demonstration with proof of calculations.❤

  • @CR8VE
    @CR8VE 3 дні тому

    This video is full of incorrect information. I suggest doing your homework

    • @cleversolarpower
      @cleversolarpower 3 дні тому

      Let's share what you found incorrect here in the comments. So everybody can learn from your viewpoints.

  • @jameswebb80
    @jameswebb80 3 дні тому

    Is it possible to run a 24 V 16s BMS system on 16 3.2 V cells configured in an 8S2P configuration or do you need to separate BMS units?

    • @cleversolarpower
      @cleversolarpower 3 дні тому

      I don't think that is possible. You need a 24V 8S BMS and wire your cells in 8S2P. So wire 8 sets of 2 cells in parallel, en then series connect them. One balancing lead for every two cells.

    • @jameswebb80
      @jameswebb80 2 дні тому

      @@cleversolarpower thats what i thought but wasnt sure

  • @Steve-yo4ld
    @Steve-yo4ld 3 дні тому

    I'm confused, so if I have a 3000-watt inverter in my trailer with 12 volt 460 to 560 amp hour, Lithium batteries aren't correct? Usage would be the majority of 12 volt with short usage of 110 volt AC! Coffee pot, slow cooker, microwave, etc...? My concern is to ensure I have enough power in reserve for cold weather camping to run the furnace and other 12 volt heat pads....etc...

    • @cleversolarpower
      @cleversolarpower 3 дні тому

      It will work, but it's just not efficiently sized. Your current will be high, so you need to have thicker wires. If it was 48V, then adding a converter to 12V would have been more efficient and cheaper.

    • @Steve-yo4ld
      @Steve-yo4ld 3 дні тому

      @@cleversolarpower Now I'm really confused! In a 12 volt system, isn't a converter always used! I don't have the system yet, I'm trying to figure out what way to go!

  • @stevenski_brewster
    @stevenski_brewster 3 дні тому

    Does Victron offer an all in one control center / inverter / charger for this 48v application? Rather than having 2 components. Thanks

  • @herbertvonsauerkrautunterh2513

    I will be using 440w panels with the same charge controller. I already have 20kw of rack batteries which aren't enough.. I don't run much at the moment. I will be buying more batteries to get to 40-50kw. My inverter of a growatt LF 12kw. It will be set up and fused for 300a max.

    • @cleversolarpower
      @cleversolarpower 3 дні тому

      300A fuse size seems ok. The charge controller is great. You can build your own battery as well. Check my video DIY vs BUY lifepo4.

  • @nomsTube
    @nomsTube 3 дні тому

    Why would you run a fridge for only 8 hours? Usually fridge and freezers are always on.

    • @cleversolarpower
      @cleversolarpower 3 дні тому

      No they are not. They usually have a duty cycle of 30%, which means they are on for 8 hours a day. Check my video about: how much power does a fridge consume? And you will see what I mean with the graphs 😉

  • @johntheaccountant5594
    @johntheaccountant5594 3 дні тому

    At 1:10 where did you get the "charging voltage" of 57.6 Volts from?

    • @cleversolarpower
      @cleversolarpower 3 дні тому

      It's the charging voltage of a 48V lithium lifepo4 battery.

  • @robertpaulis439
    @robertpaulis439 3 дні тому

    Nick...please help me understand how you connected the 2 sets of panels to the charge controller??? Your diagram appears to have 1 set going into the "load" outlet which I question. Thanks

    • @cleversolarpower
      @cleversolarpower 3 дні тому

      One set consists of 6 panels in series. It would have been too big to have it one the screen. The charge controller has two MPPT inputs.

    • @robertpaulis439
      @robertpaulis439 3 дні тому

      @@cleversolarpower how does one connect 2 sets of panels if the controller has just 1 panel hookup?

  • @Supanova70
    @Supanova70 3 дні тому

    If i have flooded 12v batteries that are combined 168AH. Is that really what is available or do i will i only get 80% out of them which would be 135.? I am setting up a battery monitor. thanks

    • @cleversolarpower
      @cleversolarpower 3 дні тому

      If you have flooded lead acid batteries, you should only use 50% to increase the lifespan. You can use more, but that would reduce it's lifespan. Check the capacity of the battery with a voltage meter.

  • @waltertoki1
    @waltertoki1 3 дні тому

    In cloudy San Francisco, I have a 9.1 kilowatt solar panel system (mounted level on a flat roof) that cost ~$21K after subtracting a 30% tax credit. On a sunny June day, it can produce more than 60 kwh. I estimate that over the year, I will get about 10,000 kwh. Since the electric utility, PGE, charges a whopping $0.50/kwh, the solar panels have an excellent return on investment.

    • @cleversolarpower
      @cleversolarpower 3 дні тому

      $0.5/kwh is huge! I assume you are using a grid tied string inverter which back feeds the excess power into the grid? Is your feed in tariff 1-1? Would it be interesting for you to add a battery?

  • @iohann.bab.7042
    @iohann.bab.7042 3 дні тому

    Too expensive for me, hi quality components are expensive, i think a 24 system with 2v led acid batteries and a easy solar 2 gx everything here is over priced.

    • @cleversolarpower
      @cleversolarpower 3 дні тому

      I might feature this in another video. Thanks for the suggestion.

  • @themightychendor101
    @themightychendor101 3 дні тому

    @cleversolarpower what if the Lithium is 0.2C with a 100A BMS i have 12.8V200ah Deep cycle lithium from Li-time

    • @cleversolarpower
      @cleversolarpower 3 дні тому

      A lithium battery is 1C, not 0.2C. If the battery has a 100A BMS, you can draw a max of 100A.

  • @captronsilveira7087
    @captronsilveira7087 3 дні тому

    Nice explaination. However I did not understand how the charging voltage is derived.

    • @cleversolarpower
      @cleversolarpower 3 дні тому

      It's the standard charging voltage for a 48V lifepo4 battery. For a 12V battery, it's 14.4-14.6V.

  • @ihabahmed1132
    @ihabahmed1132 3 дні тому

    how did we get the charging voltage 57.6 V ? are you assuming using a 48 v battery ?

  • @OffGridLivingEspana
    @OffGridLivingEspana 3 дні тому

    are the 20amp circuit breaker also for surge protection/lightning?

    • @cleversolarpower
      @cleversolarpower 3 дні тому

      No, just for isolating the solar panels. I might do a video about surge and lightning protection later.

    • @OffGridLivingEspana
      @OffGridLivingEspana 3 дні тому

      @@cleversolarpower ok thanks will look forward to that one -

  • @ihabahmed1132
    @ihabahmed1132 3 дні тому

    How can i get sun hours for Cairo/Egypt ?

    • @cleversolarpower
      @cleversolarpower 3 дні тому

      pvwatts.nrel.gov enter your location in the top bar. Works all around the world.

  • @cleversolarpower
    @cleversolarpower 3 дні тому

    🎁 Free Diagrams: cleversolarpower.com/free-diagrams/ 📖 My Best-Selling book on Amazon: cleversolarpower.com/off-grid-solar-power-simplified ✍Work with me: cleversolarpower.com/product/solar-system-review-service Parts: Solar Panels (12x): cleversolarpower.com/go/CS400W Battery: cleversolarpower.com/go/EG448V (cheaper version) Charge Controller: cleversolarpower.com/go/450/100 Inverter/Charger: cleversolarpower.com/go/5000VA Generator: amzn.to/3W4zjxr Solar PV cable: amzn.to/4eQcYv1 4AWG welding cable: amzn.to/4buslX9 DC Breaker (2x): amzn.to/3L9Ql74 125A Class-T fuse: amzn.to/3XJPUaX Class-T fuse holder: amzn.to/4cgihlD

  • @budsyusher
    @budsyusher 3 дні тому

    Hi I like option 3. I’m currently (no pun intended) putting together a 24 volt system with a3000 watt hybrid inverter and 2 200ah 24 volt batteries and would love to see a diagram for fusing and breaker values and of course the wire and proper amount of pv. My inverter is a eco worthy with mppt. Thanks

    • @cleversolarpower
      @cleversolarpower 3 дні тому

      i have made the video about system number 3. Check it out on my channel page. i have not done a 24V system on the channel. One is coming soon. Checkout my free diagrams, i believe there is a 24V system in it.

  • @jamesevans2119
    @jamesevans2119 4 дні тому

    Make sure when you size your wire the ocpd is rated for that temperature many are only rated at 75 degrees

    • @cleversolarpower
      @cleversolarpower 3 дні тому

      Overcurrent protection devices are not rated for a specific temperature. The wires are. I always recommend using welding cables, and i have linked them in the description. However, i think you mean that the wire have different temperature ratings, which is true. Lower temperature rating means less current carrying capacity.